SMC Flex Configuration Loss

I am currently experiencing problems with a couple of SMC Flex softstarters which are connected over DeviceNet to a CompactLogix system.  It seems that one of two faults may occur.  I have not personally attended any of the problems and are onlyrelaying information given to me.

 

1. The SMC Flex seems to lose their configured data for apparently no reason.  I have told the client to ensure that after he has reprogrammed them that he must save the data to Eprom and he has assured me that he has done this but the configured data loss still occurres from time to time.

 

2.  According to the client it seems that the comms between the PLC and SMC Flex "freezes".  It does not accept a start command over the network but when a hardwired start command is issued it starts ruling out the possibility that the "enable" is missing.

 

The firmware revision is 3.006 and ADR is enabled.

This one is so good … we couldn't think of a title good enough!
fuzzy_logic
Posts: 2,825
Registered: 06-26-2008
0

Re: SMC Flex Configuration Loss

Sambo, obviously the best is to be on site and see what happens exactly, which fault code is displaied etc... :smileysurprised:

 

Anyway, there is a known issue on ADR and SMC-Flex firmware revision 3.006 and earlier, as reported in Aid 30710... also there are two new firmwares for v5 and v6 that replace the original inside some SMCs which exibits the same error ( Aid 55159).

 

Maybe the problem out there is coming from improper ADR functionality... :smileytongue:

 

Hope that helps....

- fuzzy logic

Please remember to close your thread, using the Accept as Solution button over the answer that solved it... and click the Star ( ) under the user avatar to assign Kudos to those who provided help. Thanks... :smileywink:
Motion Master
vikas
Posts: 103
Registered: 06-23-2008
0

Re: SMC Flex Configuration Loss

Sambo,for the first problem given i think the required solution is only save to eeprom.

For the second problem mentioned,make sure SMC-Flex should be 3-wire controlled otherwise it wouldn,t accept start command from PLC.

Hope it helps.:smileyhappy:

VIKAS RAWAT
Ambition should be made of sterner stuff - Julius Caesar
DF1 Devotee
Sambo
Posts: 4
Registered: 10-29-2008
0

Re: SMC Flex Configuration Loss

Agree to being on-site.  My coleague, a junior engineer, tells me that there are no fault code displayed.  Which to me is strange.  The only reason I can think of is that comms actually does freeze up in the SMC and that it still thinks it is communicating to the PLC although it is not.  Highly unlikely but possible I suppose.

 

I will try to do a firmware upgrade and see whether that will solve the problem.

Motion Master
vikas
Posts: 103
Registered: 06-23-2008
0

Re: SMC Flex Configuration Loss

Sambo,did you find out whether SMC is 3-wire or 2-wire controlled?
VIKAS RAWAT
Ambition should be made of sterner stuff - Julius Caesar
New Member
PLC_SCADA
Posts: 3
Registered: 06-22-2008
0

Re: SMC Flex Configuration Loss

Hello Friends,

 

I am using about 30 number of 150-SMC-Flex devices on DeviceNet with 20-COMM-D Series-B module. I have installed the modules and the LEDs PORT/MOD/NET-A are steady Green. I have programmed the 150-SMC-Flex for Soft Start and Soft Stop Parameters. I am trying to give DeviceNet Out Signal to start the motor connected to 150-SMC-Flex.

 

For this Motor to start I have enabled Logic Command bit 1 to ON State.
In my PLC program, controller tags: Comm_Rack_DeviceNet:2:smileysurprised:.Data[0] to Comm_Rack_DeviceNet:2:smileysurprised:.Data[4] are mapped for DNET Node Output and
Comm_Rack_DeviceNet:2:I.Data[0]to Comm_Rack_DeviceNet:2:I.Data[4] are mapped for DNET Node Input.

 

 By this mapping, my plc logic makes bit Comm_Rack_DeviceNet:2:smileysurprised:.Data[0].1 == ON making sure that Comm_Rack_DeviceNet:2:smileysurprised:.Data[0].0 == OFF, Comm_Rack_DeviceNet:2:smileysurprised:.Data[0].8 == OFF, Comm_Rack_DeviceNet:2:smileysurprised:.Data[0].9 == OFF.

For some reason the motor is not getting started and the 150-SMC-Flex LEDs remain Steady Green and LCD displays "Stopped".

 

Am I missing anything? Please help me to rectify this issue. I appreciate your any help in advance!

 

Best Regards,

 

Pramod