Hi! I'm trying to use the profiler without success and can't find detailed information on how to configure.
Does anybody know of some literature about the Profiler function of PF755?
Thanks,
Marcinio
Re: PF755 Profiler
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
11-23-2009 08:40 AM
I don’t know of any specific literature on configuring the profiler. The user manual has some information on this on page B-45 and B-46.
You have to be sure that you are using profiling. Parameter #309 = 6 (Profiler)
What specific problems are you having?
Re: PF755 Profiler
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
11-24-2009 08:29 AM
Hi! I've tested the other modes of operation, Speed, Torque, PTP, Direct and it works very well. When I try to configure as a profiler (P309 and other profiler parameter), even a simple speed profiler it does not execute the steps. I noted the drive starts (it's possible to rear the switching noise) for less than a second and stops. The status of profiler indicates completed and nothing happens!
Some type of lab guide will be very helpfull.
Thanks!
Re: PF755 Profiler
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
11-24-2009 09:45 AM
I completely agree that a lab would be useful. I do not have a lab. Sorry.
From your description, it sounds like the profiler is setup, but misconfigured. Some easier to miss things to note:
user manual - page 3-124:
[Type] = Speed Profile
[Action] = Time Blend, Wait Dig-in, or Step to Next
[Value] is the Total Time to complete the move. Time is specified in 1/100ths of a second (1000 = 10.00 sec). Negative values result in time = 0 sec (no move)
Step 1 parameters are 1230 - 1239. The Type is at the top, and the Action is near the bottom.
Valid steps are 1 through 16. The default starting step is 0. (I believe that it will go to step 1 in this configuration though.)
I would like to help as much as I can. Generally, the more detailed information that you provide; the easier it is for me to help.